Dear Experts,. How to confgiure the ATM 60 encoder for working as a slave under s7 315. Shall I am able to read n write using SFC14/15? I got the GSDfile. While putting it in the Hardware configuration what should I enter n the paramaters? Some hexadecimal values are there to be entered. Have any one configured with simatic manager please help me out. ![]() ![]() the memory mapping of ATM 60 is not understanding to me. I am attatching theProfibus_encoder_connection.pdf
AttachmentProfibus_encoder_connection.pdf (630 Downloads) |
1/8/2014 1:03 PM | |
Joined: 4/22/2010 Last visit: 12/15/2022 Posts: 5697 Rating:
|
Hello, If your CPu is a 315 2dp, there is no need to use FC14/15. Follow the steps as shown in attached document. Pay attention to the profibus speed and adress of your Encoder. Regards, Marcjan AttachmentSick_encoder.pdf (682 Downloads) |