Posts: 382 Rating: (47) |
Dear j_d, Sydney was right! Just to add on that a proper termination from one node to anotheris also very important. I have attach a pdf file withinformationof a proper termination. Hope this helps! with regards, how come? AttachmentProfibus Connector [6ES7 972-0BA41-0XA0].pdf (177 Downloads) |
5/26/2009 8:57 AM | |
Joined: 9/27/2006 Last visit: 1/25/2025 Posts: 12330 Rating: (2702) |
Hello j_d; Now that Sidney and how come? have given you good information on the connections for Profibus-DP, how do you plan to establish communications between the CPUs? If you are using the integrated Profibus-DP interface on the CPUs, your only choice would be to setup one of them as a Profibus master, all the others as Profibus slaves, andconfigure a maximum of 244 bytes IN/244 bytes OUT for each slave CPU. The following link will show you how 2 CPUs can be setup as Profibus master and slave (the master here is a S7-400, but the priciples are the same): http://support.automation.siemens.com/WW/view/en/6518822 If you would prefer exchanging data peer-to-peer between the CPUs over Profibus-DP, then you cannot use the integrated DP ports, you must add a CP 342-5 communication processor to each rack. Here is an application note explaining how to connect and which functions you can use for this: http://support.automation.siemens.com/WW/view/en/20987358 Hope this helps, Daniel Chartier |