9/1/2006 9:43 AM | |
Joined: 9/1/2006 Last visit: 3/14/2025 Posts: 193 Rating:
|
I am trying to setupmaster-slave IO-based communication in a multi-project. AttachmentMp_dp.zip (420 Downloads) |
12/24/2014 1:02 PM | |
Joined: 1/28/2009 Last visit: 7/5/2025 Posts: 6871 Rating:
|
Hello Mo.Sa, The following link explains a similar situation, please read it and check if it provides you some helpful clues: What do you have to consider when connecting a S7-400 CPU to an external master as DP slave? The GSD file for SIMATIC CPUs is available here: http://w3.siemens.com/mcms/topics/en/comdec/downloads/pages/gsd-data.aspx Please , update your situation if there is any problem regarding your issue, Best regards, Hamid Hosseini |
This contribution was helpful to
1 thankful Users |
11/28/2017 1:51 PM | |
Joined: 9/27/2006 Last visit: 7/10/2025 Posts: 12373 Rating:
|
Hello Sanel; To create a Profibus data exchange configuration between a CPU 315-2DP master and a CP 342-5 slave, follow the step-by-step example below (and change the CPUs for the ones you are actually working with in HWConfig):
https://support.industry.siemens.com/cs/ww/en/view/6519580 There are 2 samples in the link, one using no data consistency, the other using SFC 14 and SFC 15 for data consistency.; I suggest you start with the first one, no consistency, so you learn how to access each data individually. Once the project is ready to work, in the program of the slave copy the encoder data you want to transfer to the master to one of the output areas configured in the slave; the master will receive the data in its corresponding input area. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 11/28/2017 2:52:26 PMLast edited by: Jen_Moderator at: 11/29/2017 11:38:57 AMInserted right link. |
|