3/14/2016 5:44 PM | |
Joined: 11/29/2011 Last visit: 4/23/2024 Posts: 1354 Rating: (229) |
Hi, Maybe terminating module? See this SIMATIC ET 200S distributed I/O Interface module IM151-1 STANDARD (6ES7151-1AA06-0AB0) manual under "4.4.9 7 Incorrect module configurations of ET 200S on the PROFIBUS DP ". I hope I could help! |
- What you read here, please check with manuals and your requirements. |
|
3/14/2016 11:43 PM | |
Joined: 11/29/2011 Last visit: 4/23/2024 Posts: 1354 Rating: (229) |
Hi, The manual says under Status and error displays : "Check the structure of the ET 200S for missing or defective modules or whether an unconfigured module is inserted...." As it was working before the logic dictates that it is a loose connection somewhere. Make sure that the terminal modules installed securely, cards installed securely also the terminal module installed securely. Apart from that, follow the guide of the above manual under chapter "4.4.9 Incorrect module configurations of ET 200S on the PROFIBUS DP ". Please keep us up to date with your progress. |