5/25/2016 7:56 PM | |
Joined: 9/27/2006 Last visit: 4/19/2024 Posts: 12256 Rating: (2664) |
Hello 2rostkar; Sorry I misunderstood your problem description earlier. So, you have interference in your PA bus when the drives (or some of them) start up? And you have limitations on the number of PA instruments you can hook up to a DP/PA Coupler? Have you made sure that no Profibus cables are within 15 cm of the drive power cables? Let's start by providing you with a brief but very comprehensive troubleshooting guide for PA Networks: http://www.automation.siemens.com/w1/efiles/weighing/techn_publications/Profibus_en.pdf There are other documents on installation, maintenance and troubleshooting of a PA network, much more detailed, from Profibus.com and Procentec that you can look for on the web. Something in your installation is not correct if you have EMI problems. First thing to think about is proper termination of the PA bus. Using Siemens SplitConnect technology, you really should look into purchasing 2 of the following termination circuits to add at both ends of your PA bus: 6GK1905-0AE00 https://mall.industry.siemens.com/mall/en/WW/Catalog/Products/10009276 Then you should use the techniques shown in the article above to look for grounding and connection issues; EMI often is associated with ground loops, signals or harmonics coming back to the sensors through ground connections. Please take the time to prepare investigations of your network, or bring in an experienced integrator who will be able to troubleshoot the bus. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 5/25/2016 7:57:44 PMLast edited by: dchartier at: 5/26/2016 12:12:56 AM |
|
This contribution was helpful to1 thankful Users |
5/27/2016 11:12 AM | |
Joined: 10/11/2014 Last visit: 7/11/2023 Posts: 79 Rating: (1) |
Hello daniel do you suggest to buy profibus analyzer to investigate our network? |