Hi! //What CPU diagnostics buffer says? //Where from did you get info about "have 4 - 5 illegal frames in network"? I suggest you to use Profibus diagnostics repeater. It can be cost-effective if you are working with such a big networks. The diagnostic repeater recognizes the following types of faults: • Break in the signal line A or B, • Short-circuit in the signal line A or B to shield, • Missing terminators, • Loose contacts, • Invalid cascading depth, • Two or more measuring circuits in a segment, • Too many nodes in a segment, • Node too far away from the diagnostic repeater, • Faulty messages. Hereyou can find a complete manual andhereis a commercial-llok-like leaflet with few another options. Good luck! BR, olloy
|