Hi BorjaY, looking at your configuration, I don't think that there is too much trafic. It isn't a very large system. Maybe you could check the network traffic by using an analysing tool link Amprolyzer Please check you hardware, the resistance at the end of the profibus line, ... There is no relationship between OB1 execution and the cycle of the network. Looking at the information about your profibus within the hardware you will find the maximum token rotation time. Within this time every slave is poled once minimum. Normaly it is much more often. Reading data with the SFC's "only" makes a copy of the actual data to the CPU. It dosn't have any effect to the communication at the bus. So please check the topology of your bussystem, resistance, ... think there the reason will be found. Good luck Sabine |
5/20/2011 8:40 AM | |
Joined: 5/28/2009 Last visit: 1/18/2025 Posts: 127 Rating:
|
Hi. Please Find The Attachment...
|
Regards, |
|
5/20/2011 8:57 AM | |
Joined: 10/7/2005 Last visit: 3/19/2025 Posts: 3042 Rating:
|
Hello BorjaY there are a few general checks that you cna do to verify that the installation is up to scratch (the vast majority of comms problems in Profibus networks are caused by poor or incorrect installation/termination). PI (Profibus International) has a couple of really good Profibus installation (assembling) and commissioning guidelines available for free at: http://www.profibus.com/nc/downloads/downloads/profibus-installation-guideline/display/ Download them and follow their instructions to verifyyour network. While there is nothing wrong with Amprolyser (and its free too, mind you you need to have a Profibus CP), it lacks the ability to verify the physical signal quality. If you are regularily dealing with Profibus Networks and/or need to maintain a numberof them, I suggest you have a look at Procentec's Profitrace 2 for this purpose. I hope this helps |
Cheers |
|
Follow us on