Hello Masoodes; Have a look at this screenshot from Siemens Product Support, for the IM 153-4 PN IO interface module (for ET 200M). You would need to remove the IM 153-1 from your remote profibus IO rack, replace it with the Im 153-4, connect your radio and the new IM with Ethernet cable, and configure a Profinet network in your project connecting to the IM 153-4. For basic information on creating a Profinet connection (including setting an IP address and a Name for the Profinet IO module), see here (sections 5.5 and 5.6 of the Profinet manual); PROFINET System Description - SiemensHope this helps, Daniel Chartier |