Posts: 9 Rating:
|
I am trying to configure a profinet connection between an 1212 and CU-320-2-PN but a connection cannot be established, the diagnostic states: Not reachable Differences were found between the loaded configuration and the offline project. Online article number: ? Offline article number: 6SL3 040-1MA01-0AAx This is a configuration I have done many times before, the difference this time is the drive firmware, 4.6 to 4.8. I am using TIA v13 SP1, since I could not find the GSDML file for the firmware version I am using, I took a GSDML file from another installation of TIA v15, and used this method to adapt it for my telegram configuration: https://support.industry.siemens.com/cs/ww/en/view/92022677 Once installed in V13 I could find the drive object in the hardware catalog and add it to my project. The offline drive object appears with the correct firmware and part number but it still will not recognize the actual drive when I go online. What might I be doing wrong? Is FW 4.8 compatible with V13 SP1? Thanks! |
Last edited by: Jen_Moderator at: 8/14/2018 1:42:04 PMOptimized link. |
|
8/14/2018 6:49 AM | |
Joined: 5/12/2006 Last visit: 3/27/2025 Posts: 22602 Rating:
|
Hello, the GSDML cn be found here: https://support.industry.siemens.com/cs/ww/en/view/49217480 Do you assign Name of Station and IP Adress to the CU320 (the same you use in the project configuration)? If you use GSDML you can not go online , only display the diagnostic state. TIA V13 doesn't support the S120 drive directly, you ust configure the drive in starter and download it. Christoph |
Last edited by: ChristophD at: 8/14/2018 6:50:51 AM |
|
8/14/2018 5:48 PM | |
Posts: 9 Rating:
|
I was able to confirm the online PN and IP information matches in both the PLC network configuration and the CU-320. What else should I consider? |
Follow us on