Please somebody help!!
Regards,
Lalit Narayan
12/15/2011 9:30 AM | |
Joined: 4/24/2006 Last visit: 3/21/2025 Posts: 8904 Rating:
|
Dear LalitN, The used CPU (6ES7 151-8AB00-0AB0) can not be used as a Profinet IO Device. (slave) Only as Profinet IO Controller (master). See this link: 6ES7 151-8AB00-0AB0 When you have 6ES7 151-8AB01-0AB0 it can be used as Profinet IO Device. Best regards, Wizard |
This contribution was helpful to
1 thankful Users |
12/15/2011 10:02 AM | |
Posts: 2348 Rating:
|
But with 8AB01 (FW from v3.2) my statement above is true |
This contribution was helpful to
1 thankful Users |
12/15/2011 11:36 AM | |
Joined: 4/24/2006 Last visit: 3/21/2025 Posts: 8904 Rating:
|
Dear LalitN, Perhaps this thread might help: /tf/WW/en/Posts/56582 Or you can use a PN/PN coupler. Best regards, Wizard |
12/16/2011 7:15 AM | |
Posts: 9 Rating:
|
Dear Sir, Please let me know that where will i get the GSDML file of 'IM 151-8 PN/DP CPU ' (6ES7 151-8AB00-0AB0) . Regards, Lalit Narayan |