7/13/2023 3:06 PM | |
Joined: 3/30/2015 Last visit: 10/17/2023 Posts: 70 Rating:
|
Hello team, 2- Is there any way to downgrade the software to V16 AND unlock the block? 3- Are there any documents that can tell me the internal structure of the ZSW and STW? Would really appreciate feedbacks. |
Last edited by: Jen_Moderator at: 07/14/2023 08:40:47Link optimized. |
|
7/14/2023 4:06 PM | |
Joined: 9/21/2012 Last visit: 12/10/2023 Posts: 3799 Rating:
|
2: Unlocking Siemens made blocks is not an option. 3: The structure of the telegram is what you define in Starter, so only you can know it. |
7/17/2023 1:10 PM | |
Joined: 3/30/2015 Last visit: 10/17/2023 Posts: 70 Rating:
|
Thank Hati, However, for this G120x drive, Starter does not work. So I am looking for solution on how to configure this telegram for the drive or just use the Siemens block but in TIA V16.
|
8/15/2023 1:17 PM | |
Joined: 3/30/2015 Last visit: 10/17/2023 Posts: 70 Rating:
|
I finally got this to work using the free telegram 12/12 word on TIA V16. I have to split the telegram into WORDs to establish communication and the rest was pretty much easy as I would do a normal G120 drive. It is important to note that the G120 Web Serve Link module was important in getting the drive configured. |