9/7/2017 10:28 AM | |
Joined: 1/30/2006 Last visit: 3/17/2025 Posts: 310 Rating:
|
The FENA11 is a multiprotocol adapter and you need to set up the fieldbus you have. By default it's set up to Modbus / TCP. See https://library.e.abb.com/public/908f01c37bf74563baedda5f16463d82/EN_FENA01_11_21_UM_D_A4.pdf Chapter regarding ProfiNet |
BR. Sven |
|
9/8/2017 5:40 AM | |
Posts: 14 Rating:
|
Yes, device is accessible but in Plc got io device failure - IO device not found.In drive side FBA setting IP address is set to 192.168.1.2. |