Joined: 4/6/2006 Last visit: 2/5/2024 Posts: 604 Rating: (56) |
Hi, With 2 CPU's you can't have Profinet IO communication. If you need fast communication you should use at least 1 CP343-1Lean card in one of the CPU's because you can set these as a Profinet IO Devices, the other CPU can then be a Controller. At this way you have a solution which is steady and can have update time from something round 4 ms. Depending on the amount of data and the selected update time. If data isn't transferred fast enough you will get a Bus Failure. In the manual for the CP343-1 Lean is described how you can integrate this system based on PNIO_SEND and PNIO_RCV (FC11/FC12). Check out Chapter 6. Manual Part CP 343-1 Lean 6GK7343-1CX10-0XE0 |
Best regards, |
|
5/7/2008 4:36 PM | |
Posts: 48 Rating: (0) |
it's better to use pn/pn coupler or the cp343-1 lean ??? |