Hello, You could read a so called system status list SSL that returns one bit per IO device. Device OK = 0, device in error = 1. The ID of the list is 0694 (hex). Reading the list is done by SFC51. How to use id SFC51 is explained in this manual: http://support.automation.siemens.com/WW/view/en/44240604 In chapter 34, you have a general introduction And in 34.25 you have the details of lists xy94 |
Best regards |
|
This contribution was helpful to
1 thankful Users |
7/1/2011 10:35 AM | |
Joined: 4/19/2008 Last visit: 11/21/2024 Posts: 1525 Rating:
|
Hi IYYAPPAN, Here is the FAQ for Diagnostic package PNIODiag for diagnostic evaluation for PROFIBUS DP and PROFINET IO or you can used the Above Example Given by jklm Using SFC 51...... |