6/11/2012 9:53 AM | |
Posts: 1547 Rating:
Hello Milosh, is the PROFINET device name entered correctly? Can you ping the device? |
6/11/2012 11:20 AM | |
Joined: 8/16/2010 Last visit: 2/23/2025 Posts: 640 Rating:
Yes... I can ping both device, name is good. Same config. I use with S7-300 and it work's good. |
6/11/2012 3:37 PM | |
Posts: 1547 Rating:
I made some further researches regarding this topic. I searched in S7-1200 system manual: http://support.automation.siemens.com/WW/view/en/36932465 If you look on the first sentence on page 426 it indicates that the 1200 cpu cannot establish Profinet connection to a non-Siemens device. Maybe you should try open user communication(T_SEND_C..., page 427) |
6/12/2012 7:29 AM | |
Joined: 10/7/2005 Last visit: 3/26/2025 Posts: 3043 Rating:
Hello Milosh good news first: It should (must)be possible to configure and use non Siemens Profinet I/O devices with an S7-1200 (as of FW 2.0 which is whenI/O Controller functionality was implemented for the 1200). The entry in the manual that Rated Xpointed you too only relates to "other" (non Profinet) communications capabilities (e.g. S7 communications between 1200's and Siemens HMI, open TCP/IP, UDPetc. see also HERE for more). It is a bit unfortunate (well, confusing) that it is all listed under theheader of "PROFINET" in the manual. Not so good news: I have no idea why your application isn't working. As you got it to work with an S7-300 I/O Controller, it should work just as well with an S7-1200 as theI/O Controller. Best I can do for you is to point you to page 470 onwards of the STEP 7 Basic V11.0 SP2 manual which describes the required Steps on how to import a Profinet GSDML file to make sure you haven't missed anything. Should you have a Siemens I/O device handy, it also wouldn't hurt to do a test of it with your S7-1200, just to make sure it isn't a problem of the1200 itself. I hope this helps |
Cheers |
6/12/2012 3:10 PM | |
Second attachment. |