3/24/2019 8:14 PM | |
Posts: 1 Rating: (0) |
Hello Pigroplc, I think something went wrong. If you want to provide a secure connection by using profisafe when defining the I-device transfer field, you must define the F-PS type or F-CD type to provide a profisafe connection and you cannot use the CD type S7-1500. The secure communication between the F-CPU security program of an IO controller and the security program (s) of the F-CPU of one or more FI devices takes place through connections between the IO controller and FI. Device connections (F-CD) (as in standard application via PROFINET IO) I added the document to below https://support.industry.siemens.com/cs/es/en/view/109478798 |
Last edited by: Jen_Moderator at: 3/25/2019 1:05:38 PMOptimized link. |
|
This contribution was helpful to1 thankful Users |
3/26/2019 10:09 AM | |
Joined: 4/3/2008 Last visit: 8/1/2024 Posts: 386 Rating: (16) |
As promised I enclose a small trace related to the subject. I guess this could be useful for someone of you guys. Again thanks to everyone who participated in this post. pigroplc AttachmentHow to setup the STO control of S120 Simotion and safety plc.pdf (190 Downloads) |