2/2/2015 4:58 PM | |
Posts: 88 Rating: (12) |
Hi See in this thread : https://www.automation.siemens.com/tf/WW/en/Posts/99205 I hope you find what you search. Bye |
2/6/2015 6:12 PM | |
Joined: 11/29/2011 Last visit: 12/16/2024 Posts: 1361 Rating: (232) |
Hi, Have a look at this "S7-1500, ET 200MP, ET 200SP,ET 200AL Diagnostics" manual under chapter 4.1 Configuring alarms for system diagnostics. In point 6 you can read: "In the settings, specify the alarm category that is to be displayed and if it needs to be acknowledged. The check boxes in the "Alarm" column are enabled by default. When you disable all check boxes, the status of the HMI system diagnostics view is still updated with the "Info Report" functionality." |
Last edited by: MicroMan at: 2/6/2015 6:26:45 PM- What you read here, please check with manuals and your requirements. |
|
2/9/2015 4:11 PM | |
Joined: 11/29/2011 Last visit: 12/16/2024 Posts: 1361 Rating: (232) |
Hi, In manual https://support.industry.siemens.com/cs/us/en/view/68074843 under page 1026: You define the acknowledgment model for an alarm class. Alarms that are assigned to this alarm class will be acknowledged on the basis of this acknowledgment model. The following acknowledgment model is used in WinCC: ● Alarm without acknowledgment This alarm comes and goes without having to be acknowledged. There is no visible response from the system. ● Alarm with simple acknowledgment This alarm must be acknowledged as soon as the event that triggers the alarm occurs. The alarm remains pending until it is acknowledged. So what you need to do is organize the alarm messages you do not want acknowledge into a specific message class, set up this message class like "Alarm without acknowledgment" and that should be it. Cheers |
Last edited by: MicroMan at: 2/9/2015 7:03:41 PM- What you read here, please check with manuals and your requirements. |
|
2/10/2015 8:16 PM | |
Joined: 11/29/2011 Last visit: 12/16/2024 Posts: 1361 Rating: (232) |
Hi,
So same manual as last time page 1331 "Acknowledgment by the PLC": https://support.industry.siemens.com/cs/us/en/view/68074843 If this time I answered your question, please rate my answer! If I misunderstand you again, please ask again! Have a good one! |
- What you read here, please check with manuals and your requirements. |
|
This contribution was helpful to1 thankful Users |
2/12/2015 10:26 AM | |
Joined: 11/29/2011 Last visit: 12/16/2024 Posts: 1361 Rating: (232) |
Hi,
"The following alarm block is available: So If you choose the alarm class resetable you can reset the message, maybe the predefined alarm classes do not cover your requirements. So maybe you need to look at Custom Alarm Classes. Have a look at "WinCC Basic V12.0 System Manual, 01/2013 manual" under chapter "9.3.1.4 Alarm classes" On page 1024:
So that is a bit difficult way around, but I hope it will works for you! |
- What you read here, please check with manuals and your requirements. |
|