Hello all. I've made a simple program to communicate with a Modbus Slave. I read 4 registers(with diferend data lenght's from the PLC that act's like a Modbus slave. I first execute the 4 COMM_Load blocks (at startup, one at a time) and then when I try to read the first register of bool variables (or any other, one at a time), the busy output is ON and a while later the error bit is ON and the error is 8070. It's not described in the manual what this error ID is so, do any of you perhaps know what it. Also please tell me if I have the correct sequence of blocks. It's strange to me that If I only work with one Comm_Load and Master block the comunication works. Thanks in advanced. Best regards. Aleix
---------------------------------------------------------- New subject after splitting from S7 1200 modbus sample program required |
Last edited by: Min_Moderator at: 10/24/2014 9:59 AMSplitted Last edited by: Poljachina77 at: 10/23/2014 6:10 PMnotification ON |
|
10/24/2014 12:05 PM | |
Posts: 3093 Rating:
|
Hello Poljachina, error 8070 is listed in the manual, it means that not enough memory is available. Regards, Kaulquappe |
9/11/2017 1:22 PM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8175 Rating:
|
New question published by Orthodudz is split to a separate thread with the subject MB_MASTER get error status 8070. Best regards |