Hello, as PISCEAN2010 said we need more info to help you. anyway you can find what you need in masterdrive compendium. to add a comparator at dig.out please go to chapter "Function Diagrams" :
Hope this helps, Best Regards |
★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★ |
|
1/9/2018 7:34 PM | |
Posts: 4 Rating: (0) |
hello again , the only cables are connected to the drive (cuvc) are a) at X101 terminals(1,2,3,6,7). b) at X102 terminals(15,16,19,20). b) at X103 terminals(23,24,25,28,29,30). X102.15-X102.16 is an AnInput (speed input) from the PLC. there is no profibus or other commun.interface. X101.6-7 are used for DI X101.3 is used for DO. i would like to make X101.5 (this is free) to be a DO . This DO will be 24V when the motor does not rotate(speed ==0) and will be 0V when the motor starts to rotate(speed>0). i checkmasterdrive compendium. i think i should change P653 parmeter value but i m not sure what 'binector' to choose. Also have I to change the two indexes to non zero values to make the port X101.5 be a DO? best regards. |
1/11/2018 6:23 PM | |
Posts: 4 Rating: (0) |
thank you i will try this and i will post again ... thank both of you for your help |