12/10/2012 11:12 PM | |
Joined: 5/28/2008 Last visit: 9/9/2024 Posts: 4515 Rating: (839)
|
Hello, Welcome to our forum. You have in your configuration CPU 313 + SM321 (6ES7 321-7RD00-0AB0). I mean that 6ES7321-7RD00-0AB0. is not the CPU type, but it is the DI module part number.
You have to use PC adapter with part number6ES7972-0CB20-0XA0. With this PC adapter you can program Siemens PLC S7-200, S7-300 and S7-400. And for sure you need STEP 7 software. If you have problems in selecting it, please tell us to help you.
Please note that the rated voltage of S7-300 CPUs is 24VDC. Permissable limits are: Lower limit: 20.4VDC & Upper limit is 28.8VDC. So please check that your DC power source is within these limits. Hope this helps.
|
Ayman Elotaify |
|
This contribution was helpful to1 thankful Users |
12/18/2012 8:01 PM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715)
|
Hello, You can find the specifications of your module here; SIMATIC S7-300 S7-300 Automation System Module Data There you can see your module has this specification for input delay: Input delay "0" to "1" transition 1.2 ms to 4.8 ms "1" to "0" transition 1.2 ms to 4.8 ms So 45Hz must not be a problem. Regards, Marcjan |
Problem solved? |
|