Hello AutoGen_4960596, I guess you are talking about A01796 because A01496 is not mentioned in list manual of S120. The alarm value is important to understand the cause of this alarm. Because the machine was working before it could be alarm value (3), which indicates that communication to the PROFIsafe F-Host is not established. See S120 list manual for details. https://support.industry.siemens.com/cs/ww/en/view/109827046 If you just restart the drives and keep the F-PLC powered this fault appears because F-communication is just initialized during start up phase of all components. You can use ACK_REI tag of the F-I/O DB or ACK_GL instruction for user acknowledgement. See chapter 6.5 of SIMATIC Safety configuring and programming manual for further details. https://support.industry.siemens.com/cs/ww/en/view/54110126 |