9/2/2020 1:35 PM | |
Joined: 9/9/2014 Last visit: 2/12/2025 Posts: 246 Rating:
|
Hello, Look at the topics and manuals below: Manual and example: 3-Point Stepper Control with SIMATIC S7-1200/S7-1500 Manual: SIMATIC S7 S7-1200 Programmable controller For your question The PTC sensor has a resistance greater than the module can measure - from 100 to 60,000 ohms (sometimes more) On page 1416 you must see SM 1231 RTD specifications: Technical data SM 1231 AI 4 x RTD x 16 bit SM 1231 AI 8 x RTD x16 bit That is, the module can only measure RTD sensors and resistance up to 600 ohms For example: Analog input module AI 4xRTD/TC 2-/3-/4-wire HF (6ES7134-6JD00-0CA1) SIMATIC ET 200SP Distributed I/O system This module can receive measurements from PTC sensors ******************** That is, in your case you need to either invent something - or change the module (the second option will be more appropriate) Also, for a more accurate solution to your problem, you need a sensor model, and not just data that it can measure up to 90 degrees. |
Last edited by: Unreality at: 09/02/2020 13:35:53Best Regards |
|