Sir I have a halleffect water flow sensor 264 pulse written wiring up 24 vdc logo and connected IT inputinput 2.2k resistor after up down counter pulse count not counting in counter.could please tell me how I can resolve the problem Thanks Mrabiudeen ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 1/18/2018 2:30:47 PMNew subject after splitting |
|
2/5/2018 5:59 AM | |
Joined: 12/18/2014 Last visit: 9/22/2024 Posts: 33817 Rating: (4201)
|
Try this (see attachment). Attachment24 VDC sensor with open collector NPN to LOGO! I5.pdf (262 Downloads) |
2/7/2018 7:30 AM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8175 Rating: (172) |
New question published by mrabiudeen is split to a separate thread with the subject LOGO! - exchange data with TIA Portal. Best regards |