5/18/2010 3:51 PM | |
Posts: 510 Rating: (117) |
I have attached 3 pages from the 1200 Easy Book to get you started. Q4.0 is the address if you have a signal board installed. Q0.0 and Q0.2 are the outputs on the 1200 I/O. Use the CTRL_PWM block to start and stop the pulse output. Good Luck, billwest AttachmentPWM Pages from s71200_easy_book_en-US_en-US.pdf (1031 Downloads) |
5/20/2010 5:44 PM | |
Posts: 510 Rating: (117) |
The PWM configuration includes the output address. It is located above the Hardware Identifier in the device configuration. This address is used to change the initial pulse width.You use the Enableof the CTRL_PWM to turn the output, Q4.0, on and off. You use the output address to change the pulse width. I have attached 3 slides from a training presentation that includedPWM. Hopefully this will resolve your questions. Good Luck billwest AttachmentPulse Width Modulation (PWM).pdf (966 Downloads) |
11/26/2013 7:32 PM | |
Joined: 7/7/2010 Last visit: 4/26/2024 Posts: 14639 Rating: (2349)
|
I tested your findings and found the exact same thing, Portal V12 will not allow you to configure a s7-1200 signal board as a high speed control output. Since this is a feature mentioned in the s7-1200 documentation, I would submit it as a Support Request. Let us know what they respond with, either work-around or future firmware/software fix. |
science guy |
|
11/26/2013 7:54 PM | |
Posts: 10 Rating: (0) |
Thanks for your help! I sent in a support request. I'll report back with what they tell me. |