Hi again!
Parallel I am redoing the entire project with a 1513F PLC in combination with ET200M. Both project have the same I/O. When I look at the DB generated for the FAI6 I am using, I see that my convert has the same signals as my original Simatic Manager based program. But the auto generated DB in my new new project, is different. Specifically, I do not have a QBAD signal for every analog input, see attachment. How can I obtain these?
AttachmentDoc1.pdf (102 Downloads) |
1/22/2016 6:25 AM | |
Joined: 5/12/2006 Last visit: 9/3/2024 Posts: 22352 Rating: (3008) |
Hello, S7-1500 have no QBAD it is replaced with Value State: Replacement of the QBAD_I_xx or QBAD_O_xx tag by the value status Here you find a FAQ for Migration of Safety from 300 to 1500: https://support.industry.siemens.com/cs/de/en/view/109475826 Regards |