5/25/2016 7:40 AM | |
Joined: 9/27/2006 Last visit: 3/20/2025 Posts: 12344 Rating:
|
Hello JRomero; Yes, it is recommended that FB55 be called in OB 100, the S7-300 Start-Up OB. See the following document: SIMATIC NET Program blocks for SIMATIC NET S7 CPs - Programming Manual https://support.industry.siemens.com/cs/ww/en/view/62543517 When using FB55, the following use cases must be distinguished: ● Standard application call FB55 in the startup OB (OB100). When OB1 starts, the CP then already has its IP configuration and possibly also its connection configuration. ... OB 100 is active before OB 1 (or any other block in the S7 program) so the CP would receive its IP address from FB55 at the power-up of the PLC. Hope this helps, Daniel Chartier |