2/25/2008 2:20 PM | |
Joined: 9/27/2006 Last visit: 10/10/2024 Posts: 12286 Rating: (2685) |
Hello user; There are various vways, including studying the OB86 local temp variables or reading the Profibus-DP diagnostic data. But there is an easier way that should give you a good hand. Siemens has developped a Profibus-DP diagnosis FB 125, that you can download free and install in your project. It is available here: http://support.automation.siemens.com/WW/view/en/387257 It also comes with FC125, a simpler version of the block;FC125 will not signal the slot number of a defective module in a ET 200M rack, for example; the FB125 has that option. Simply follow the setup instructions (call the FB125 in all 3 OBs required) and use the data from the output of the block to program the messages you need. There are also templates to use with WinCC Flexible/Protool, maybe you can make use of them in your application. Hope this helps, Daniel Chartier |
1/19/2016 10:07 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4767 Rating: (123) |
New question published by RSGokul is split to a separate thread with the subject Hold the last input state in S7 400 H CPU when ET200M (IM153-4) power failure?. Best regards |