hi, i have two kind of GEt & PUT communication senarios: 1. s7-1500 to s7-1200 (is it possible?) 2. s7-1200 to s7-1200 should i consider any data limitation? is that limitation depands on CPU client or both server & client? is that limit refers per connection or its the total for all? thank you my friends. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 2/27/2018 9:15:15 AMNew subject after splitting |
|
2/27/2018 10:04 AM | |
Joined: 7/9/2015 Last visit: 3/21/2025 Posts: 4204 Rating:
|
Hi, S7-1500 to S7-1200 and S7-1200 to S7-1200 will work with put/get (both controller can be client or server). Please check PDF Page 6523 - there you wil find informations about user data Size for S7-1200 and S7-1500. https://support.industry.siemens.com/cs/de/en/view/109747136 Regards, Towome |
|
|
This contribution was helpful to
1 thankful Users |
2/28/2018 10:30 AM | |
Posts: 9 Rating:
|
thank you! your answer was clear. graet day! |