9/14/2010 3:50 PM | |
Joined: 9/27/2006 Last visit: 9/10/2024 Posts: 12282 Rating: (2682)
Hello Pouya_PCS; What you are trying to implement is called Software Redundancy (SWR) in Siemens' world. Here is a link to the manual of SWR: http://support.automation.siemens.com/WW/view/en/1137637 Search for SWR or S7-300R using the search box at the right and you will find many threads from users setting SWR up. Hope this helps, Daniel Chartier |
9/15/2010 10:08 PM | |
Hello Pouya_PCS; Chapter 4 of the SWR manual explicitely defines the use of a redundant pair ot IM 153-2 (-2BA02-, for example) in order to implement SWR. The following Application manual, even if it discusses redundant ET 200M nodes for PCS 7, can be used for explanations of the use of redundant ET 200M inSWR: http://support.automation.siemens.com/WW/view/en/28430682 You will find illustrations of the connection of redundant CPUs over Profibus (on the integrated DPinterfaces) with dual IM 153-2s + active bus modules, in order to setup redundant I/Os. Hope this helps, Daniel Chartier Edit: By the way, the manual doies not require exact duplicate CPU racks and I/Os for SWR. Only those units that will be required for redundancy must be duplicated or made redundant. You can have "single-sided" I/Os or CPs, that will not be transfered by the redundant function blocks. D.C. |