1/23/2017 4:24 PM | |
Joined: 9/2/2012 Last visit: 3/14/2025 Posts: 711 Rating:
|
Dear All, Am facing issue communication issue in a small profibus network. Maximum 16 nodes- all are 3rd party devices. 1.5Mb/S is the network speed. Maximum length of the network is 30-40m. Application is paint booth. System was working for last 6 years. Last 1 month facing communication issue. Installation seems to be ok. cables are routed not with power cable. Shield is connected to connectors properly. Terminations are kept on for last nodes. After this communication issues, replaced cable and connectors. The 1 meter rule is violated for 12 nodes. But all are inside the panel, no drives are in network. Routing order-- node10-11-12--cpu--node6--41-42-43-44-node71-72-73-74-75-76-77-78. The problem coming for nodes 41 to 78. Checked the network with Profitrace, found differential stable voltage for CPU, NODE6 are below threshold. But voltage on either side of CPU is @ higher level. Is it really possible ? How can i troubleshoot the problem.. Attaching the profitrace report, any suggestions are welcome .. AttachmentFORUM.pdf (546 Downloads) |