8/26/2008 4:05 PM | |
Joined: 4/24/2006 Last visit: 3/14/2025 Posts: 8894 Rating:
Hi Balderdash, What's the firmware of CPU? hereyou can download latest firmware. Best regards, Wizard |
8/26/2008 4:39 PM | |
Posts: 196 Rating:
Have you check your check witch error OB that has been triggered, you should be able to get some diagnose data out from the module. If you use the FB7 that is provide with card there is at description how to evaluate the errors, and how to read them from the CP341. Because the SF led only indicate there a error. Here is link to the manual. http://support.automation.siemens.com/WW/view/en/1117397 |
9/4/2008 4:18 AM | |
Posts: 5 Rating:
I have the same problem, same diagnostic messages, with CP341-1CH01 and a CPU317-2DP. Also the same behaviour where it may power up ok about50 pct of thetime.It has run fine for a couple of years, but lately they have been doing more mechanical maintenance on the system and therefore powering off the system than they ever did before. CP341 is in rack 1 slot 7, address 400. As well, I have recompiled, reconfigured, redownloaded the HW Cfg, etc. I have just got the firmware from Siemens support net for the CP341 and the CPU. I will try flashing both units the next time I am on site. attached is diagnostic log. Please comment. AttachmentCPU317sep3bDiagnose.zip (183 Downloads) |
4/5/2019 9:42 AM | |
Joined: 3/2/2007 Last visit: 3/11/2025 Posts: 979 Rating:
Kindly, did anyone solve this problem ? " Random SF on power up from CPU341 " |
... thank you ... |