Dear Kamerke, an orage DC-Link LED is not showing an error. Orage means that DC-Link voltage is present and you should thak care in case of touching components! The green and orange LED on module siteshow a "ready" system state. If there is a control problemyou should verify LEDs on CU. An "overload"-error can be caused by several reasons.Maybe temperature monitoring has triggert or I²t. Remedy would be reducing load dutycycle.. The error code gives you somemore detailed informations. Take a look in the alarmbuffer. General infos about the meaning of LED are summerized in equipment manuals: http://apps01.industry.siemens.com/content/00000100/Content/syn_s120.aspx In the "parameter manual"you find additional infos, causes and remedys regarding alarms and warnings. |
With best regards, |
2/11/2014 10:44 AM | |
Hello, please try link: https://www.automation.siemens.com/doconweb/pdf/SINUMERIK_SINAMICS_02_2012_E/GH1.pdf?HTTPS=REDIR&p=1 or ask google for "equipment manual CU320" If an alarm is present it should be indicated in BOP. Even you can navigate via BOP to alarm buffer. An easier way is to downloadthecommissioning tool STARTER: https://www.automation.siemens.com/mcms/mc-solutions/de/software/ibn-tool-starter/seiten/ibn-tool-starter.aspx?HTTPS=REDIR |