just one more thing to note before you decide to spend your money on a CP342-5 to replace your CP343-5: It can only be used for the redundancy link between the CPU's but NOT for the connection of ET200M's (while the CP342-5 principally supports DP Master functionality itis NOT supported as a DP Amster interface in an S7-300 Software redundant system)! As such, you are limited to using your S7-300CPU's onboard Profibus DP port for the connection of ET200M Profibus DP Slave stations (an S7-400 offers you more choices such as CP443-5 and IM467, have also alook at Which modules can you use when implementing software redundancy? for more on this) I hope this helps |