7/19/2018 8:03 AM | |
Joined: 4/28/2015 Last visit: 9/20/2024 Posts: 397 Rating: (56)
|
Hello, you could use channel 0 and channel 1 of this module to do counting. For this, please see chapter 2.2.1 of the function manual of this module. But be sure, that the counting frequency is enough for your application... If you also want to use the position value of the encoder, maybe it will be better to use one of these technology modules (TM): TM COUNT 6ES7550-1AA00-0AB0 S7-1500, TM COUNT 2X24V SIMATIC S7-1500, TM count 2x24V Counter module, 2 channels for 24 V incremental or encoder 3 DI, 2 DQ per channel https://support.industry.siemens.com/cs/ww/de/ps/6ES7550-1AA00-0AB0 6ES7138-6AA00-0BA0 ET 200SP, TM COUNT 1X24V SIMATIC ET 200SP, TM count 1x 24V Counter module, 1 channel for 24 V incremental or encoder, 3 DI, 2 DQ https://support.industry.siemens.com/cs/ww/en/ps/6ES7138-6AA00-0BA0 TM POSINPUT 6ES7551-1AB00-0AB0 S7-1500, TM POSINPUT 2 SIMATIC S7-1500, TM POSINPUT 2 Counter and position detection module for RS422 incremental encoder or SSI absolute value encoder, 2 channels, 2 DI, 2 DQ per channel https://support.industry.siemens.com/cs/ww/en/ps/6ES7551-1AB00-0AB0 6ES7138-6BA00-0BA0 ET 200SP, TM POSINPUT 1 SIMATIC ET 200SP, TM POSINPUT 1 Counter and position detection module for RS422 incremental encoder or SSI absolute value encoder, 2 DI, 2DQ https://support.industry.siemens.com/cs/ww/en/ps/6ES7138-6BA00-0BA0 |