hii i am usings7-1500 plc ,g120p drives telegram 999 . i am reading speed,amps,kw ,now i want read kwh value ,selected r39 but showing stack over flown 7fffh. any suggestion? thank you ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 01/11/2021 09:42:44New subject after splitting |
|
1/13/2021 10:13 AM | |
Joined: 1/29/2006 Last visit: 2/11/2025 Posts: 449 Rating:
|
.... or use SinaParaS FB, from Sinamics library (Optional packages->Sinamics). Have fun! uel123. |