10/10/2019 7:29 PM | |
Joined: 8/31/2005 Last visit: 8/20/2024 Posts: 2198 Rating: (328) |
You can transfer the metered value of the AI to the PLC, If you have Tel352, you may change one of the send values in Tel 352 in the configuration of the send data (communication>transmit direction) If you have Tel1, or an other small telegram, you first have to expand the telegram in the PLCs telegram configuration. Have a look on this forum thread too: https://support.industry.siemens.com/tf/ww/en/posts/g120-actual-current-telegram-352/221683/?page=0&pageSize=10#post879886 |
Last edited by: miami at: 10/10/2019 19:29:35Last edited by: miami at: 10/10/2019 19:35:51Last edited by: miami at: 10/11/2019 14:24:56 |
|
10/11/2019 10:06 AM | |
Joined: 9/12/2013 Last visit: 7/4/2024 Posts: 32 Rating: (0) |
Hello, Thank you for the reply @miami. I will try to explain in brief what we intended to do, There are two mixing tanks with agitator having VFD control and need to check minimum weight of the tanks (measured using differential pressure) to interlock agitator. So if we connect transducer directly to AI of VFD and send raw count to PLC where we gonna scale it and display on HMI as well. Would this work? I know we can simply add analog input module with PLC rack but the issue is we need to integrate 18 more tanks with VFD control for agitator in future and as of now we are doing just two of them. So every time we have to lay cables, add analog module, punch hole in panel etc to add each VFD afterwards. To resolve this we asked if there is any possibility to read AI through VFD and send it to PLC for scaling. Thanks in advance. Regards, Parag Zope. |
11/15/2019 7:04 AM | |
Joined: 4/28/2015 Last visit: 9/20/2022 Posts: 1278 Rating: (298) |
Hi, you can work on with telegram 1 and SINA_SPEED FB if you want. You should expand the telegram by adding additional setpoint/actual data -> see my screenshot. Then this additional data will get its own Hardware ID (also see screenshot). From the PLC you can read the data with the GETIO block. (see screenshot). AttachmentRead_AI.pdf (110 Downloads) |
Best regards, |
|
11/15/2019 2:42 PM | |
Joined: 4/28/2015 Last visit: 9/20/2022 Posts: 1278 Rating: (298) |
Hi, try to change p922 to "999 free BiCo" |
Best regards, |
|