Hello everyone! My current project is to read the level in the tank using level sensor. The analog sensor that I have is SITRANS LR100 Radar and the controller is using PLC SIMATIC s7-1200 CPU 1214C AC/DC/Rly. At first, I just wired the LR100 to the PLC, spesifically in AI built-in, in series with the power supply 24VDC. Previously, I've already setup the LR100 using SITRANS Mobile IQ. Later, the PLC cannot read the analog signal, and then I've just realised in the guide book that LR100 communications using bluetooth, HART, or Modbus RTU. The AI built-in card don't provide the 4-20mA. Then I do some researches to HART module Siemens, and I found6ES7331-7TF01-0AB0is HART enabled module, but can only connected to CPU ET200M. Then SITRANS LT500 also can be connected to LR100, but this isn't I wanted to this project because it's not controlled from a PLC. The I found 6ES7231-5ND32-0XB0 (AI SM1231) that supported 4-20mA and can be connected to 1214C. Regards, Farkim |