Hello peter; Could you please explain exactly what you are planning to do? Are you refering to the operationnal limits of the on-board analog inputs of your CPU, or the sampling rate of the A/D chips that handle the conversion to digital levels? In the following document you will find information on analog sampolig rates for the S7-31xC PLCs: SIMATIC S7-300 CPU 31xC and CPU 31x: Technical specifications Measuring principle 31xC CPUs use the measuring principle of actual value encoding. They operate with a sampling rate of 1 kHz. That is, a new value is available at the peripheral input word register once every millisecond and can then be read via the user program (e.g. L PEW). The "previous" value is read again if access times are shorter than 1 ms. So yoiur maximum possible rate of reading analog values should be 2 ms per value (Shannon's theorem of sampling). Hope this helps, Daniel Chartier |