Hello hernan_e I'm afraid to say that I'll be the bearer of bad news for you. A CP342-5 can only be a DPV0 DP master. You do however need a DPV1 capable DP Master to doDataset read/writerequests (these are done via the acyclic services which a DPV0 DP Master can NOT do). The only solution is to use the CPU's onboard DP port or an S7-400 with either the onboard DP port or a CP443-5 extended. I hope this helps |
Cheers |
|