The trick to this is the "Configuration of the message received" for the PtP module. The defaults are often much slower because they are generic rather than specific to your application. For example, you know the first character for any acceptable frame, and you know the last 2 characters as well. What you want is the stuff in between, right? You will want to configure the frame start and end detection, receive buffer, and then make sure you are looking at the configured I/O addresses for the module's. This may help guide your thinking during the configuration: https://support.industry.siemens.com/cs/document/89674023 There is a fairly recent firmware update you might want to install: https://support.industry.siemens.com/cs/document/82258405 This is the link Siemens recommends you review while performing the configurations: https://support.industry.siemens.com/cs/mdm/59057093
|