9/2/2016 5:46 PM | |
Joined: 11/29/2011 Last visit: 8/19/2024 Posts: 1359 Rating: (232) |
Hi, See the SIMATIC ET 200M distributed I/O device HART analog modules manual under chapter "7.1 Overview of the data record interface and user data of the HART communication" and "7.2 Data record interface". If you need any help with using the SFC's/SFB's, let us known. |
- What you read here, please check with manuals and your requirements. |
|
9/3/2016 11:05 AM | |
Joined: 11/29/2011 Last visit: 8/19/2024 Posts: 1359 Rating: (232) |
Hi,
See the SIMATIC ET 200M distributed I/O device HART analog modules under chapter "6.1 HART analog input module SM 331; AI 8 x 0/4...20mA HART (6ES7331-7TF01-0AB0)". It says: "Any measuring range selection per channel To be 100% sure check the Field Instrument's manual and loop drawing of the 4-20mA loop. To get a bit more background information see: |
Last edited by: MicroMan at: 9/3/2016 11:13:58 AM- What you read here, please check with manuals and your requirements. |
|
This contribution was helpful to2 thankful Users |