Hello arun_1152, What type of S7-300 and which way of controlling the Safety Functions do you use? If it is a failsafe PLC with PROFIsafe you can evaluate the PROFIsafe telegram received from the G120. The structure in the manual: https://support.industry.siemens.com/cs/document/109744795, chapter 4.3.2. If it is a non-failsafe PLC or you don’t use PROFIsafe, you can use PROFIdrive telegram 700 to get the information about the Safety Functions. How to set up telegram 700 is described in the manual: https://support.industry.siemens.com/cs/document/109740018, chapter 5.8.5. The description is for S120, but also works with G120. The transferred data is described in chapter 5.8.6. After both use cases you have the information about the Safety Functions from G120 in the PLC so you can proceed to the HMI. |
With best regards, |
|