7/7/2014 8:56 PM | |
Posts: 53 Rating: (1) |
Dear All, I have working for converting a manual batching plant to Automation. I am planning to use S7 200 for this. I have suggested the PLC:CPU226AC/DC/Relay: 6ES7 216-2BD23-0XB0 and analog module:EM231AnalogInput,8Inputs:6ES7 231-0HF22-0XA0But I got there are existing load cell. That are not generating 4-20 ma. So, I can't connect these to PLC. I need 4 load cell to connect with PLC. So, what is module I need to connect the Load cell to PLC? Here is my load cell model and spec. Shear Beam Load Cell - 30310 Link: http://www.adiartech.com/productdetail.aspx?pid=60&cid=1 Is there anything I may need for this PLANT? Attachment6030310 - pdf.pdf (221 Downloads) |
7/8/2014 8:57 AM | |
Posts: 5225 Rating: (1192) |
|
7/8/2014 11:58 AM | |
Joined: 9/1/2005 Last visit: 9/18/2024 Posts: 4104 Rating: (195) |
closed cause question posted twice. The second thread with the subject Load cell Ready-mix concrete- Batching Plantis published within the conferenceProcess Instrumentation / Analytics / Weighing Systems SIWAREX. Best regards CS Moderator |
My Forum is the place to personalize your profile, |
|