1/29/2020 2:00 PM | |
Joined: 8/31/2005 Last visit: 8/20/2024 Posts: 2198 Rating: (328) |
You can use
See https://mall.industry.siemens.com/mall/en/de/Catalog/Products/10021255?tree=CatalogTree for available encoders from Siemens. In most cases only one encoder is required for such an application. Incremental encoders loose the position when they are switched off. A synchronization movement is required after mower on im most applications. |
|
|
This contribution was helpful to1 thankful Users |
1/30/2020 10:19 AM | |
Joined: 1/15/2020 Last visit: 2/18/2020 Posts: 6 Rating: (0) |
Thanks a lot miami, that's a lot of help! With my application it would probably be best to use an absolute encoder as the system will be switched off periodically and we need to know the position upon the next power-on state. In terms of connections to the S7-1200, am I correct in thinking that a sensor that is supplied with flying leads is sufficient for HSC input? I guess I would connect each lead/wire into the PLC and use the PLCs HSC function? Finally what is "TM Count" and "TM Posinput" please? Apologies I'm not familiar with these terms. Thanks |
1/30/2020 4:12 PM | |
Joined: 8/31/2005 Last visit: 8/20/2024 Posts: 2198 Rating: (328) |
"TM Count" and "TM Posinput" are module to read in encoders in a ET 200SP station: 6ES7138-6BA00-0BA0 ET 200SP, TM Posinput 1 6ES7138-6AA00-0BA0 ET 200SP, TM Count 1x24V |
|
|
This contribution was helpful to1 thankful Users |