4/3/2015 12:08 AM | |
Joined: 11/29/2011 Last visit: 2/20/2023 Posts: 1347 Rating:
Hi, To share what I found. Manual WinCC Professional V13.0 page 3904-3905 "Transfer with synchronization": "In order to synchronize transfer of data records between the HMI device and the PLC, the following requirements must be met during configuration: ● An area pointer has been set up: "Communication > Connections" editor in "Area pointer". ● The PLC with which the HMI device synchronizes transfer of data records is specified in the recipe: "Recipes" editor in the inspector window the option "Coordinated transfer of data records" under "General > Synchronization > Settings"" There is a status tag in this structure. I hope someone find this information useful! |
- What you read here, please check with manuals and your requirements. |