6/15/2013 9:24 AM | |
Joined: 5/23/2011 Last visit: 9/28/2023 Posts: 36 Rating:
Dear experts How should i wire up 7KF02-0AB0, when it is used as redundancy? |
6/21/2013 10:33 AM | |
Joined: 11/8/2011 Last visit: 8/28/2023 Posts: 387 Rating:
Hi Please have look here Analog Input Redundancy |
6/29/2013 6:49 PM | |
Hi godfather, You can use Field Interface Module (FIM) for analog Input redundancy Hope this helps |
6/29/2013 7:17 PM | |
Joined: 3/18/2008 Last visit: 8/25/2022 Posts: 1750 Rating:
Hello, In one of my project i have used UL Redundancy Module to achieve redundacy with above Analog input Module. Please have a look at following Thread. Technical data of UL Redundancy Module Hope this helps. |
VANDE MATARAM..... |
6/30/2013 10:34 AM | |
Posts: 559 Rating:
Dear godfather, Please find the attached wiring diagram for the same. If you have current transmitter then connect as per 2-wire transmitter as shown in page-1. If you have voltage transmitter the connect as per shown in page-2. AttachmentRED_AI_Wiring.pdf (199 Downloads) |
6/30/2013 10:39 AM | |
Posts: 559 Rating:
Please find the attached file which explains the basic concept for the connection of Redundant Analog inputs.
AttachmentBasic_Concept_RED_AI.pdf (188 Downloads) |
10/15/2015 3:13 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4792 Rating:
New question published by Smithyy is split to a separate thread with the subject 7KF02, measured mV does not match with standard mV VS deg C table. Best regards |