3/10/2009 7:54 PM | |
Posts: 19 Rating: (0) |
hi, I need help about a redundacy analog output. I'm using two output analog card (6es7 332-8TF01-0AB0) and I'm testing to a card Analog input (6ES7 331-7TF01-0AB0). At this when I force an output off 8mA I'm reciving 16mA. In Attachment is the electrical connections. please help me. AttachmentRedundacy AO.pdf (161 Downloads) |
3/10/2009 11:47 PM | |
Posts: 2661 Rating: (279)
|
Hi bilro, Which version of PCS7 are you using? For HART you need atleast V7.0 SP1 and IM's 153-2BA02/82-0XB0 must be used. See chapters 1.3.4 and 2.2.4 in the followingconfiguration note: Configuration of Redundant I/O Modules Regards |
3/11/2009 10:14 PM | |
Posts: 2661 Rating: (279)
|
The CH_AO should be configured only for the lower address. The RED_OUT takes care of the rest. See attachment. You should place the CH_AO in OB35 (for example) and the module in HW config in a PIP corresponding to OB35. I suggest you read the config note from last post thoroughly. Regards AttachmentPages from 28430682_Projektierung_red_IO_en.pdf (166 Downloads) |
3/16/2009 7:23 PM | |
Posts: 19 Rating: (0) |
Hi again, I already made all the changes and still dont work. I also tried with hart connections. I need a urge help what do you advise me. |
3/16/2009 7:42 PM | |
Posts: 2661 Rating: (279)
|
What isthe mA reading? Can you post your project? Regards |
3/17/2009 11:41 AM | |
Posts: 19 Rating: (0) |
I already made like you said. only one project with CPU that I have the problem but after archive it still have 30Mb. How you want to do it. |
3/17/2009 1:39 PM | |
Posts: 19 Rating: (0) |
Hi Phantom75, I talk with my informatic depart and I can give you a link to you download the project. what you think about this? |
3/17/2009 3:42 PM | |
Posts: 2661 Rating: (279)
|
Hi bilro, I sent you a PM with my email address and you can send the download link via email... Regards |
Follow us on