Hello Ahmed, It's been a long time since I've worked with software redundancy but as far as I can remember, it was not possible to start both CPUs with absence of all ET200Ms. It's just my own speculation, I think both CPUs will think that something is wrong with their DP master interfacesand will act as a standby CPU. From your status word, it's clear that redundant link has been established which is a good sign (but it doesn't mean you have finished) but both CPUs can't communicate with any DP slave. Even if my speculation is wrong, it's still not possible to tolerate the absence of all DP slaves and any work under this situation may lead you to deceiving results. You will have to wait until you get ET200M and start the real fun. Best regards. H-H |
11/11/2010 6:07 AM | |
Posts: 13 Rating: (0) |
Hello Ahmed, I can help you in this case. You need to use atleast one redundant bundle of ET200M on active bus connector for IM and IO each on profibus DP portbcozatleast one module (DI/DO/AI/AO) in that particular rackis necessaryto achieve software redundancy otherwise result is not fruitful. Please donot hesitate to contact. Regards Omkar AttachmentSWR_E.pdf (323 Downloads) |