Hello, So, S7-1200 will be Modbus Server. The other side will be Client (two clients). All Modbus clients access the Modbus server through Port 502. All these things (managing the connections) to be done in Clients. What is necessary to be done in S7-1200http://support.automation.siemens.com/WW/view/en/59381441(As Pegaia wrote there must call two server blocks). Best regards, Hristo Mihalev
|