8/25/2013 11:55 AM | ||||||||
Posts: 34 Rating:
|
Dear All please i want your support about configurationinattached system if it is correct or not ? in field layer the communication Protocol ProfiBus In application Layer communication Protocol S7 TCP/IP Hardware ssystem consist of : 1- Redundant CPU :
2- Commonication Processor :
3-Redundant Interface modules in two ET200M :
AttachmentRedundant System S7-400+CPs+ET200M.zip (670 Downloads) |
|||||||
8/26/2013 1:15 AM | ||||||||
Joined: 5/28/2008 Last visit: 3/17/2025 Posts: 4518 Rating:
|
Hello,
Hope this helps. Attachmentredundant.pdf (892 Downloads) |
|||||||
Ayman Elotaify |
||||||||
3/29/2016 3:37 PM | ||||||||
Joined: 5/28/2008 Last visit: 3/17/2025 Posts: 4518 Rating:
|
Hello, For Redundnat CPUs, you need to use two CPUs H-Type like what you have selected 414-5H And for IOs, you can go with RED-Bundle to make redundnat communication through Profibus or use Profinet with single IM or use Profibus with single IM but with using Y-Link. Who decide? The Clinet and the project Costing, and needed availability of the system. Hope this helps. |
|||||||
Ayman Elotaify |
||||||||
3/29/2016 4:10 PM | |
Joined: 9/27/2006 Last visit: 3/19/2025 Posts: 12344 Rating:
|
Hello eng. Abdul; There are 4 basic ways you can connect I/O racks to a S7-400H system, for redundancy. With a redundant ET 200M station, you can setup a "single channel switched IO" system, through Profibus-DP or Profinet. See the attached screenshot, taken from chapter 13 of this manual: SIMATIC Fault-tolerant systems S7-400H https://support.industry.siemens.com/cs/ww/en/view/82478488 If you decide not to use a redundant ET 200M bundle, you can choose any of the other 3 possible configurations, this will be a choice to be discussed with your client; the evaluation of compromise between function and cost is a basic part of engineering. Hope this helps, Daniel Chartier |
This contribution was helpful to
1 thankful Users |
Follow us on